Honeywell motorised zone valve not closing
I've got a Honeywell zone valve controlling flow to part of the central heating which isn't fully closing and the upstairs rads are coming on when the hot water is on.
I've swapped the motor inside the valve over with one which I know is working but that makes no difference. Shame as that would have been an easy 11 quid fix... I am trying to avoid buying a full new actuator but feels like that might be the solution. It's a bit odd as electrically it's working, it opens when it should and closes when it should but it's just not fully closing. If I put it on manually by the lever then let it close it stops closing very quickly, much quicker than the other one which is working fine. So something is preventing it from closing, I was wondering if it's the nipple from the valve that's seized but don't know how stiff this should feel, I can turn it a bit with pliers. Otherwise it's something inside the actuator gearing etc which is nackered. Any thoughts or suggestions? |
05-07-2024, 09:21 AM | #2 |
Major General
1440
Rep 8,167
Posts |
My central heating seems to eat those - I probably need to replace the actuator every three years. Easy to do though and you can get pattern parts for about £40. However, if the valve does not close properly by moving the actuator directly it may be that the rubber-ball part of the valve is gunked up and you'll need to replace the actual brass body which of course entails draining the system. It could also be the micro-switch that detects the mid-position and locks the motor isn't working.
If you move the brass stem there's probably only about 60 degrees of movement from A to B.
__________________
Ian
Current: 2021 G21 330i M-Sport Previous: 2018 A6 Avant S-Line MMI+, 2014 F31 320d M-Sport, 2013 F10 520d M-Sport, 2011 F10 530d M-Sport, 2008 320i M-Sport Coupe, 2002 325i, 2001 318i valvetronic, 1998 318i, 1996 525i, 1990 Porsche 944S2 |
Appreciate
0
|
05-07-2024, 09:25 AM | #3 |
Captain
434
Rep 871
Posts |
My assumption is that there's some crud on the sealing ball or spindle that is preventing it from closing, especially if you cant get it to shut with pliers.
Seen it many times on isolating valves. One possible reason is a lack of inhibitor in the heating system. One thing to try is tapping the spindle with a wrench or small hammer. Sometimes that can loosen the crud causing it to foul. Repeatedly tap-turn-tap-turn. Could also apply a penetrating oil. |
Appreciate
0
|
05-07-2024, 09:28 AM | #4 |
Lieutenant Colonel
2142
Rep 1,987
Posts |
As said above, chances are there is some build-up of something (probably scale or rust debris) in the valve itself, stopping it from fully closing. It only needs to let by a tiny bit to cause problems.
Normally a drain-down job to inspect/ replace the valve body unfortunately. Worth noting aswell...if a valve isn't opening or shutting fully, it can burn actuator motors out, as it is likely the microswitch inside the actuator isn't being triggered, so causing the motor to be powered constantly. I've seen this knacker many actuator motors over the years. Last edited by Pond; 05-07-2024 at 09:34 AM.. |
Appreciate
0
|
05-07-2024, 10:42 AM | #5 |
Colonel
813
Rep 2,137
Posts |
Frustrating, as I would do the simple changes myself, but I'm not draining it all down. The actuator appears to work perfectly when it's not connected to the valve, closes and opens all the way, so it's got to be the brass bit hasn't it...
|
Appreciate
0
|
05-07-2024, 10:59 AM | #6 | |
Colonel
813
Rep 2,137
Posts |
Quote:
It actually seems to move really freely, the other one which is working fine is super stiff in comparison. Last edited by NotGotABimmer23; 05-07-2024 at 12:00 PM.. |
|
Appreciate
0
|
05-07-2024, 04:10 PM | #7 | |
Major General
1440
Rep 8,167
Posts |
Quote:
|
|
Appreciate
0
|
05-07-2024, 04:46 PM | #8 | |
Lieutenant Colonel
2142
Rep 1,987
Posts |
Quote:
|
|
Appreciate
0
|
05-08-2024, 12:29 AM | #9 | |
Major General
1440
Rep 8,167
Posts |
Quote:
Anyway, it sounds like the ball valve itself is failing to seat. |
|
Appreciate
0
|
05-08-2024, 01:37 AM | #10 | |
Colonel
813
Rep 2,137
Posts |
Quote:
|
|
Appreciate
0
|
05-08-2024, 04:25 AM | #11 |
Lieutenant
387
Rep 544
Posts |
Do this every two years. It will add life to other components of your system too. We do ours just after a boiler service
__________________